I don't pretend to be a VFD expert but I'm hoping someone has some insight. I have a VFD in this facility on a newer system installed 3ish years ago before I was employed on site. Unfortunately when they bought this water system they didn't have the manufacturer commission the equipment so some of it didn't get tested after the install. Long story short - This drive and pump has never been online. Working with the engineers to try and get the pump going, I manually power up the pump off the VFD, the drive shoots to 40A, then eventually faults. I took an amp reading on the VFD output (while the readout said it was pushing 40A) and each phase is reading less than 2A. I've taken the motor out, meggered it, check for locked rotor and everything checks out fine. Plus I switched leads in the enclosure to a VFD I know is functioning and the motor spun up just fine. Is there a setting somewhere on the drive that I'm missing? Or is the drive just faulty? Again, the drive has 0 hours on it so it's odd it would have failed but I've seen stranger things. I'm no VFD guy either but based on what you stated it seems there is something basic or a setting not accounted for. I would use the startup or owners manual and go thru step by step to see if you forgot something or didn't "check a box"
Maybe Jraef (not sure I spelled it right) can chime in since he is the resident expert on drives
BTW my moniker is ABB because they bought out GE Zenith Controls, the transfer switch (ATS) division that we are a authorized service station for. Not the drive division! Is the meter a true rms meter? It won't read right if it is expecting a sine wave and is getting a bunch of DC pulses off the VFD instead.

Best bet is to get the manual and go thru the commissioning procedure. Start by resetting the drive parameters to factory default. No telling what someone else did to it over the years.

Make sure you go thru the tuning procedure.

If you still have trouble try running it in volts per hertz mode instead of sensor less vector mode if that has been selected What does it do if you either don't have anything connected to drive output (some won't run if no load on them though) or with another motor temporarily connected to it? Can just be some small motor for this purpose doesn't need to be same rating as what it was supposed to be connected to.

I would think resetting it to factory defaults would allow it to run your motor if nothing is wrong with anything. May need to set a few basic parameters about the motor you are driving but not much else and I would think it would run well enough initially. Might then want to tune or tweak any parameters you may feel is necessary for better performance.

I take it this is new as in "never used" yet has been thirtyish years since it was made from what you mentioned in OP?

You said it eventually faults, what is the fault?

Is possible someone connected a voltage source to the output terminals and the output circuitry is toast, way back when they were trying to set it up and then gave up on it and it just sat there all this time because they didn't know what was wrong?

ABB ACS880-01-021A-5 AC Drive - Riverside Drives

Over the past 40+ years, we've helped 's of customers.

Link to ABB

Riverside Drives, Inc. was built on over 75 years of expertise in power transmission and motion control design. The father-son partnership established a vision that combines traditional values with forward-thinking innovation—offering specialized engineering, extensive product knowledge, and exceptional customer service.

After 40+ years, Riverside Drives' has thrived as a family business and our commitment to quality, service, and family values continues. We excel by fostering long-lasting relationships built on trust, reliability, and mutual respect.

For more Abb Machinery Drivesinformation, please contact us. We will provide professional answers.

This has led to a wealth of knowledge and experience that isn’t easily found, with many of our employees contributing to the company for over 30 years. This commitment has ensured Riverside Drives maintains its reputation as the trusted partner for manufacturers across the US.

At Riverside Drives, we understand that our customers' success is our success. This dedication to excellence and innovation has helped us grow, and we're proud to continue the tradition of serving our clients with the same care and commitment that started over 40 years ago.

If you want to learn more, please visit our website Abb Industrial Drives.

8

0

Comments

0/2000

All Comments (0)

Guest Posts

If you are interested in sending in a Guest Blogger Submission,welcome to write for us!

Your Name: (required)

Your Email: (required)

Subject:

Your Message: (required)

0/2000